    I am getting ready to connect dc power to a mobile transceiver. Is there a local (SCRA) standard powerpole connector configuratiion?

    Tnx
    kd6nt

    #10818

    ag6ci
    Participant

    I’m sure we all use the “ARES” standard configuration. You can see a picture of them here:
    https://powerwerx.com/anderson-powerpole-connectors-15amp-bonded
    I also buy mostly the pre-bonded ones so that I can’t mess up.
    This configuration is also used for accessories like in-line meters and so on.
    ’73
    Keith, AG6CI

    #10819

    Fred AE6SF
    Participant

    Red Right, Tongue Top

    Memorize that phrase. See attached photo.

    Hams typically use Anderson Powerpole series PP15, PP30 and PP45 for 12VDC systems.
    Black = negative
    Red = positive

    The 15, 30 and 45 distinguish the contact that goes into a universal housing. The contacts are selected based on the wire size in AWG:
    PP15 => 18-16 AWG (Contact 1332)
    PP30 => 14-12 AWG (Contact 1331)
    PP45 => 10 AWG (Contact 261G2)
    If you look at the spec sheet, Anderson says the contacts actually
    accept a larger range of wire sizes as follows, but it is common practice to use the above values. From the spec sheet (last page):
    PP15 => 20-16 AWG (Contact 1332)
    PP30 => 16-12 AWG (Contact 1331)
    PP45 => 14-10 AWG (Contact 261G2
    The mating surfaces of all three contact sizes have the same surface area. It is the wire size, not the contact size, that dictates the current-handling capability of the connector. The spec sheet shows temperature rise curves for current versus wire size.

    Anderson recommends crimping the connections. The spec sheet says that “Only closed barrel contacts are suitable for soldering,” meaning only the PP15 contacts may be soldered. WB6FRZ may weigh in advising that soldered connections do not stand up to vibration, and therefore should be avoided.

    I use a drop of cyanoacrylate glue (super glue) to bond the black and red housings together. I have a hammer ready to quickly force the housings into position before the glue sets. I non-destructively separated glued connectors, again using a hammer, in the one instance I tried.

    Here’s the spec sheet:
    http://www.andersonpower.com/_global-assets/downloads/pdf/ds-pp1545.pdf

    Here’s a common source:
    https://powerwerx.com/anderson-power-powerpole-sb-connectors

    – Fred AE6SF